Re: Electritian needed ,

Quote:
Originally Posted by wallop79 View Post
What you have is an old Wylex rewireable fusebox, you need a more up to date RCD consumer unit installing, as the problem you mentioned would have caused a modern consumer unit to trip......
It might not have caused a modern consumer unit to trip. You could easily have a bad connection causing heat and the current in the circuit be lower than the rating of the MCB so it would not trip. Please dont assume MCB's will protect you better than fuses for all faults.