Thread: Heating Help
View Single Post
Old 15-02-2012, 20:38   #18
mark2004uk
Member
 

Re: Heating Help

Quote:
Originally Posted by Retlaw View Post
One problem I once found in a central heating system with a similar complaint, was a long run of unsupported pipe under the living room floor, the sag in the pipe caused a large air bubble to form, stopped water circulating in that part of the system. Once the pipe was supported, and the bubble bled out, problem solved.

Retlaw.
I have bleed to death lol.... warm water is getting to the rad at the bottom where the valve is... just not in the rad, and like i said the bioler cuts out... so its deffo godda be the flow thing im sure, I have cleaned the rad its like a new one, new valve done everything i can think of, even tried balancing the sytem
mark2004uk is offline   Reply With Quote